skinnywolfe OP t1_iw4j1ux wrote
Reply to comment by ttraband in Running wire to power this 20x10 shed for an office. What wire do I need? by skinnywolfe
So I have already drilled and wired outlets inside the shed for computer/monitor on one, accessories on another, and a separate circuit for the hanging overhead light
ttraband t1_iw4k1db wrote
I’d still add a third circuit (outlet or two) for future expansion, unless the walls are going to be open/a, then it’s easy to add at any time. Often rooms are wired so outlets on parallel walls are one circuit, adjacent walls are differential circuit.
tsaico t1_iw52mjf wrote
Honestly, just do a pull string if you are not doing the 3rd now. Save yourself the cost now, but make it as easy as possible to do it when the time comes. Also, do no smaller than 1" sched 40.