fatherfirst35 OP t1_j1vkkpy wrote

4 on a 20a breaker seems like way overkill. Every other bedroom was wired with at least 6 on a 15a breaker. This bedroom though will be a guest bedroom so there won’t be much load anyways. I will probably switch it up and wire the lighting separate though as suggested.

2

dilligaf4lyfe t1_j1vy3xp wrote

You're right, it is overkill, I outlined the load calcs in another comment.

3

AceDetective427 t1_j1vne8m wrote

If it was me, I would do the standard 1 per wall unless you have a specific reason or intent to have more in that area. Maybe put 2, one on either side of the bed for nightstands on that wall like you generally have in a master bedroom. If you are only doing 5 or 6 total outlets then 1 circuit should be enough, but when I saw 8 outlets I figured this was going to be like a hobby room with workbenches or something where more power would be warranted.

0