In California at least, stranded is used only inside conduit for most gauges of wire, so it's seen more in non-residential. In residential, you use solid for most wiring. Stranded would only be used when you're doing things like a run that goes underground to a secondary building on the property (stranded of whatever size is needed to feed the sub panel) since you'd be running underground conduit, incoming lines, or really low gauge wires like alarms or speakers.

3

ZAFJB t1_j1h96o4 wrote

Underground conduit is rare. Armoured cable is far more common.

0

Typh00nYTG t1_j1ioxau wrote

In residential it's rare. On utility sites it's used quite commonly for power and comms between settings and buildings. We only use stranded for that because there may be lots of bends in the conduit from point A to B. Specifically where it has to be in conduit and in Class 1 Div II areas.