Viewing a single comment thread. View all comments

imanze t1_j0lqgs7 wrote

that’s not the wording of the code. Exception: Where the 20-ampere circuit supplies a single bathroom, outlets for other equipment within the same bathroom shall be permitted to be supplied in accordance with 210.23(A)(1) and (A)(2).

OUTLETS can be shared, OUTLETS is the key word you changed.

1

dominus_aranearum t1_j0n6dxf wrote

>OUTLETS is the key word you changed.

Good lord. I didn't change anything. YOU are misunderstanding what the definition of 'outlet' is in the NEC.

NEC Article 100 defines an “Outlet” as a point on the wiring system at which current is taken to supply utilization equipment. The term “outlet” is often misused to refer to receptacles. Receptacle outlets are only one type of outlet. Other types of outlets include lighting outlets, appliance outlets, smoke alarm outlets, equipment outlets and so on.

A lighting outlet is an outlet intended for the direct connection of a lampholder, a luminaire or a pendant cord terminating in a lampholder. Luminaires can be ceiling-, wall- or even floor-mounted (See Figure 2). While the wiring for lighting outlets can terminate in outlet boxes and in other boxes under certain conditions, it can also terminate in junction boxes of luminaires.

So, in short, just because you don't understand what 'outlet' means in the context of the NEC, doesn't make what I wrote wrong. If you're still adamant, go ask someone in /r/electricians. I've been through hundreds of inspections, have you?

1