I have a new work box with a keyless lamp fixture. Neither of these have a ground. Both the hot and neutral wire have 120 v running to them. The light won't turn on and the only thing I can think of is the free ground wire. If that doesn't have anything to ground to could that be preventing the light from turning on? It's hooked up to a single pole light switch with the ground wired on that one with the two hot wires.

19

Comments

You must log in or register to comment.

Sevulturus t1_j6azjrq wrote

What are you using as your reference to find the 120v?

1

broken2302 t1_j6b1vwb wrote

There should not be 120 on the white and black. The romex wire going thru the switch box is black, white & ground. White to white. Black split by switch. Ground to ground. In your light box, Ground wire to the light fixture ground. Black wire to darker brass screw and white to other lighter brass screw.

1

ICYaLata t1_j6b2c1z wrote

Ground wire is not the problem. Switch should only control the Hot wire.
1)Do you have 120v at the line side of your switch?
2)Do you have 120v on the load side of the switch when it's on? 3)Do you have continuity of the hot conductor from switch to your fixture? 4)Are you sure your fixture works? 5) are all your connections secure and properly done?

1

Cappuccino_Crunch OP t1_j6b43t6 wrote

Ok with switch in off position and wires not connected to fixture: The neutral reads 120v and the hot zero. With it in the on position both read 120v. That's the light fixture.

The hot wire from the source always reads 120v regardless. The wire at the switch going to the fixture reads zero when the switch is turned off and 120 when on. The neutral wires are capped and the grounds are spliced with a pigtail to the green screw.

1

ICYaLata t1_j6b4ws3 wrote

Why is your neutral reading 120? There should be no voltage on your neutral unless its part of a closed circuit. Are you sure your wires? Older houses did not pull neutrals to switches and often used a white wire in the pair as a switched or hot leg. You may want to post a couple pictures.

1

ICYaLata t1_j6b7lj7 wrote

Take the lamp out, and with the switch on, check if the socket has power. If you read 120v at the socket, it's the lamp. Or the metal plate at the bottom of the fixture isn't making contact with the lamp.

1

broken2302 t1_j6b95j7 wrote

Thank you. So do you have 120 from the source (left side) between the black and ground in the swich box - maybe dm me

1

Cappuccino_Crunch OP t1_j6barge wrote

Ok separated the neutrals at the box. In the off position the line black wire reads 120, the load (to the light) reads zero and the line neutral reads 120 and the load neutral reads zero. So at this point everything is zero at the lamp.

With the switch in the on position, all black wires read 120. The line (from the source) neutral reads 120 and the load neutral reads zero. So at the lamp with the switch on the neutral is zero and the hot is 120.

This is with the lamp removed and the neutral wires untwisted but the grounds and hot at the switch hooked up.

1

Sevulturus t1_j6bna7c wrote

Yeah, that's why I said it doesn't make it back to the panel.

But if that were true, the number you would read with one probe on black and one on white would be zero, or close to zero.

Edit assuming you see 120v from black to copper.

1

XFactor-41 t1_j6en1vv wrote

Actually, I think I see the problem. Disclaimer: I’m not an electrician, just a somewhat experienced amateur, but for the life of me, I don’t see why that neutral is bundled and capped with those hot wires. That’s likely where your neutral picking up that voltage is coming from.

I will gladly step aside and admit defeat if a professional wants to contradict this answer.

1

XFactor-41 t1_j6esfs8 wrote

Ok, disregard my previous comment. How many b/w pairs are in that box? There should be 4: two on the hot side of each circuit and two that lead downstream.

Disconnect and separate everything. Then organize the wires by pair. Then, test to see which is the hot coming in from each circuit. Then you’ll have to do a little trial and error to see which of the downstream pairs goes to the light vs the switch.

Confirm this and let me know.

1

XFactor-41 t1_j6ew5xa wrote

Is that a split outlet? In other words, does the switch control one half of it and the other half is on the other circuit? If so, I have your solution.

The circuit that the switch is on was designed to terminate at that spot. With the power and the switch on, find the hot wire for that circuit. Then, connect that pair to either the top or bottom of the outlet.

With the remaining two pairs, you’re going to have to make two pigtails. Take a spare piece of black/white wire accordingly and cut off about 9-10”. Strip the ends and with a wire nut, bundle the two black wires in the box together with one pigtail, and do the same with the white. Connect the other side of the pigtails to the open half of the outlet accordingly.

1