They switched the neutral, so hot runs to the fixture, then to the switch, when the switch is in the off position the circuit can not complete path to ground, in the on position it can.

21

brock_lee t1_j6jli3v wrote

OP should also be able to confirm this by removing the bulb. There should then be no voltage detected on the switch wire, regardless of on or off position.

10

more_than_just_ok t1_j6jq13w wrote

Exactly. OP can unscrew the fixture and will probably see hot black to fixture, white to white, and black coming back from the switch to the fixture. It's an easy fix. Hot black to switch-leg white, returning switch-leg black to brass screw on fixture, chrome screw on fixture to neutral.

5

lucky_number-VII t1_j6jozia wrote

Your switch was wired "backwards". Easy mistake to make and to fix. Singe pole single throw switches work both ways, so there really is no backwards. If it were a different kind of switch you might be in trouble. This not a danger to you unless you have wild OCD.

1

rgraham888 t1_j6ju2ou wrote

except that you can shock yourself on a turned off fixture since it's always hot.

9

Guygan t1_j6k1tq3 wrote

Your submission has been removed for one or more of the following reason(s):

  • You are asking about a project that someone else did, or you're considering having someone else do.
  • You are not asking a question relating to something DIY.
  • You are not asking a question at all.
  • You are submitting a "DIY Tips" or "Tricks" post.
  • You are trying to submit a survey / fundraiser.
  • You are asking what an item is called - try /r/whatisthisthing.
  • /r/DIY allows only two types of posts - finished projects & help requests.
  • If your submission is neither of these - it will be removed.

Please read our Full Sub Rules before resubmitting.

If you believe this was a mistake, please message the moderators.

###Do not respond to this comment - you will not receive a response.

1