> OP said the outlet is GFCI not the breaker. You can't have both together.

Sure you can. It's just unnecessary and occasionally makes troubleshooting a little annoying.

> GFCI specifications were changed to Arc fault because everyone complained GFCI'S tripped too often.

GFCIs and AFCIs are two totally different things. AFCIs in no way replace GFCIs and won't protect against ground faults (unless the fault causes arcing). Maybe you mean switching a GFCI breaker out for a combo breaker that does both?

> I would love to replace all these stupid outlets and breakers in my house if it wasn't for insurance reasons.

They're there for a very good reason, especially the GFCIs. And frankly it doesn't sound like you should be replacing anything.

2

Mammoth-Pain-358 t1_j9onj88 wrote

I have done a lot of electrical work. NEC electrical code article 210.12(A), installing an AFCI breaker is required in all single-phase and 15 to 20 amp circuits with a 120V supply. This rule applies to the area of the kitchen, most rooms of a house, and hallways. Bathrooms are required to have GFCI outlets and AFCI breakers are not required. Also, you can install a GFCI outlet on a circuit with a GFCI breaker. The NEC doesn’t encourage this practice however.