cassiedanger t1_j263gwf wrote

Mine was set at 67 and 58 was the warmest I was able to get, however the thermo is in the small kitchen and directly next to the boiler so it’s cheating. The living room and bedrooms were significantly colder. My building is old and superbly shitty though.

3

Blecher_onthe_Hudson OP t1_j264qaw wrote

Did you complain to the manager or just figure that the cold snap would pass? Do you recall at what outdoor temperature it started to not keep up?

2

cassiedanger t1_j2653v1 wrote

I was recovering from Covid and was both contagious and brain foggy so I didn’t bother - we’ve had the super up here six times to “fix” the heat since I moved in 6 weeks ago. Won’t turn off won’t turn on back and forth forever. Finally get it working and then that happened. At one point a few weeks back it was 90+ inside so we left our AC units in, I put plastic and tape over those and then went back to bed. The list of things I want fixed before I pay for January is as long as my arm.

2

Blecher_onthe_Hudson OP t1_j266p2j wrote

Ughh, that sounds like incompetence rather than a real equipment problem. Surely they simply replaced the thermostat? PSEG is giving Nests away!

2

cassiedanger t1_j26en8v wrote

The thermostat was replaced twice but the issue initially was the pump was circulating the hot water to the radiators without ever shutting off? Honestly it’s been a mess.

2

Blecher_onthe_Hudson OP t1_j26i1i3 wrote

That's bizarre, it's not that complicated! Thermostat closes a 24v switch and the relay in the boiler turns the pump on, opens and it goes off. If it's not the thermostat its the relay.

2