Blecher_onthe_Hudson OP t1_j266p2j wrote

Ughh, that sounds like incompetence rather than a real equipment problem. Surely they simply replaced the thermostat? PSEG is giving Nests away!

2

cassiedanger t1_j26en8v wrote

The thermostat was replaced twice but the issue initially was the pump was circulating the hot water to the radiators without ever shutting off? Honestly it’s been a mess.

2

Blecher_onthe_Hudson OP t1_j26i1i3 wrote

That's bizarre, it's not that complicated! Thermostat closes a 24v switch and the relay in the boiler turns the pump on, opens and it goes off. If it's not the thermostat its the relay.

2