You have a single breaker that serves a fridge, microwave oven, a convection oven (I assume it's a gas oven, so the electric is just for igniter/display), and some lights? That's a whole lot for a single breaker. Even just a fridge and a microwave together are nearing the threshold for a 15A circuit. I also assume the dryer is a GAS dryer, right?
LFKhael t1_iy4u1ao wrote
Oh man, houses were wired terribly for 50+ years.
My parents' kitchen, dining room, and garage all operate on one breaker.
We found out using the microwave and plugging in an electric stovetop in the garage for a party.
ModalEclipse OP t1_iy4wmby wrote
The convection oven is a standalone appliance, like an air fryer.
These are all plugged into different outlets as well. Not sure if the dryer is gas... but yes, this place is wired poorly.
roobinsteen t1_iy5j1i4 wrote
Must be a gas dryer, because electric dryers use 240V outlets--there's no way it could be shared with 120V lights and outlets. Either way, there's just way too much on a single circuit. Those countertop convection ovens are using like 10-12 amps I imagine, so you really can't use that at the same time as anything else on the same circuit besides lights, etc.